What does E01 Mean on Hitachi SJ200?Looking for some help with some Hitachi SJ200 Errors. I'm not sure if you call these errors, faults, or alarms but I can use some detailed info and troubleshooting suggestions.
- Hitachi E01 Alarm
- Hitachi E01 Error
- Hitachi E01 Fault
Thanks in advance!
E01 Error / E01 Fault / E01 Alarm
Means: Overcurrent while at "Constant" speed
Possible Causes: Inverter output was short-circuited, or the motor shaft is locked, or the load is too heavy, or a dual-voltage motor is wired incorrectly.
Note: The Hitachi SJ200 will over current trip at nominally 200% of rated current.
Also, Hitachi SJ200 inverters will trip on over-current, over-voltage, and under-voltage to protect the inverter. The motor output turns OFF, hence the motor free-wheels to a stop. Just press the Stop/Reset key to reset the inverter and clear the error.
(http://www.obsoleteindustrial.com/photos/hitachi-alarm-fault-e01.jpg)