Title: Troubleshooting a Thermocouple Ground Loop
Post by: mike1999 on January 25, 2016, 03:06:PM
Anyone have experience troubleshooting a thermocouple ground loop. I installed a surface mount thermocouple on a motor surface to monitor overall temperature. I coupled it to a basic Red Lion readout and it worked fine.

About two weeks into its life, it started acting strange. The temperature reading started going from positive to negative and back again. I replaced the thermocouple with a new one and it did the same thing.

I then replaced the Red Lion readout with another one I had in stock. The problem remained. So i don't understand but it seems as though a ground loop has been created or something. I never heard of thermocouples getting noise.

Anyone have any thoughts on how to troubleshoot a thermocouple ground loop?
Title: Re: Troubleshooting a Thermocouple Ground Loop
Post by: Cheller on January 27, 2016, 04:33:AM
I think a thermocouple ground loop is more possible than noise. A thermocouple generates a small DC voltage as it heats up and I'm not sure how it could be a noisy signal. I'm assuming the thermocouple is grounded to the surface?
Title: Re: Troubleshooting a Thermocouple Ground Loop
Post by: mike1999 on February 01, 2016, 06:25:PM
To be more specific, I am using a Red Lion CUB5TC Thermocouple Meter with an optional single relay card inserted to trigger a fault on the plc. The thermocouple is a Type J with a #10 eye hole that I screwed to the surface of the motor. I am trying to create a redundant temperature monitor for this motor since it is located in an out-of-the-way place.

The thermocouple is located about 50 feet from the Red Lion meter and this setup worked for a while before i started having problems. Not sure where this is going but I just thought it might be a grounding issue. ???
Title: Re: Troubleshooting a Thermocouple Ground Loop
Post by: mike1999 on February 02, 2016, 05:22:PM
OK, here's an update... If I unscrew the thermocouple from the motor and hang it in mid-air, it reads the air temperature just fine. As soon as I touch it back to the metal surface of the motor, the reading goes from positive to negative and then bounces back and forth like it's confused.
Title: Re: Troubleshooting a Thermocouple Ground Loop
Post by: Cheller on February 03, 2016, 04:49:AM
Try isloating the thermocouple from ground. Get creative with some kind of insulator but still contacting the surface of the motor and see what you get.
Title: Re: Troubleshooting a Thermocouple Ground Loop
Post by: mike1999 on February 04, 2016, 04:27:AM
Cheller,
That did it, it is reading temperature accurately now. Here's what i came up with:

(http://www.obsoleteindustrial.com/roundtable/gallery/45_04_02_16_4_24_04.jpeg)

I used a magnet with a metric threaded hole that i got from McMaster for another application. I screwed the thermocouple to the magnet and I coated the bottom of the magnet with electrical tape. I also covered the braided wire with heat shrink tubing and it works great.

I'm still not sure why it worked for a while, but the probelm seems to be resolved. Thanks!
Title: Re: Troubleshooting a Thermocouple Ground Loop
Post by: mike1999 on February 12, 2016, 04:17:AM
In closing, here's a couple of parts numbers if you were looking to duplicate this deign: I got the Red Lion CUB5T from our local Red Lion distributor but the rest of the parts came from mcmaster.com.



Title: Re: Troubleshooting a Thermocouple Ground Loop
Post by: benklassne on April 26, 2024, 04:43:AM
Good work on the thermocouple tests...

(https://www.obsoleteindustrial.com/i24/thermocouple-fault-test.png)