Got Questions Get Answers => Troubleshooting 101 => Topic started by: travis on May 28, 2017, 06:33:AM

Title: What does E03 Mean on Hitachi SJ200
Post by: travis on May 28, 2017, 06:33:AM
What does E03 Mean on Hitachi SJ200?

Looking for some help with some Hitachi SJ200 Errors. I'm not sure if you call these errors, faults, or alarms but I can use some detailed info and troubleshooting suggestions.


Thanks in advance!
Title: Re: What does E03 Mean on Hitachi SJ200
Post by: drives-technician on May 31, 2017, 04:07:AM
E03 Error / E03 Fault / E03 Alarm

Means: Overcurrent during "acceleration"

Possible Causes: Inverter output was short-circuited, or the motor shaft is locked, or the load is too heavy, or a dual-voltage motor is wired incorrectly.

Note: The Hitachi SJ200 will over current trip at nominally 200% of rated current.

Also, Hitachi SJ200 inverters will trip on over-current to protect the inverter. The motor output turns OFF, hence the motor free-wheels to a stop. Just press the Stop/Reset key to reset the inverter and clear the error.

(http://www.obsoleteindustrial.com/photos/hitachi-alarm-fault-e03.jpg)