#91
Quote from: rickpend on October 01, 2016, 04:34:PM
What is Fanuc SV0417 Alarm?


ILL DGTL SERVO PARAMETER: A digital serve parameter setting is incorrect.
[When bit 4 of diagnosis information No. 203 is 1.]
An illegal parameter was detected by the servo software. Identify
the cause with reference to diagnosis information No. 352.
[When bit 4 of diagnosis information No. 203 is 0.]
The CNC software detected an illegal parameter. Probable
causes are given below (see diagnosis information No. 280).
1) The value specified in parameter No. 2020 as the motor model
falls outside the specified range.
2) The motor rotation direction in parameter No. 2022 is not set to
a correct value (111 or -111).
3) The speed feedback pulse count per motor rotation in
parameter No. 2023 is set to a negative or other incorrect value.
4) The position feedback pulse count per motor rotation in
parameter No. 2024 is set to a negative or other incorrect value.

#92
DC Drive Feedback Selection

I know this is an old post but for your application I would try armature voltage feedback first. See if it appears stable, and put a clamp on ammeter on it. Let us know how you made out.
#93
Troubleshooting 101 / Re: Parker 590+ Drive Alarms
September 14, 2016, 03:28:AM
Here's the remaining alarms, I will add a list of the applicable models as soon as I can...


  • OVERSPEED (This alarms occurs when the speed feedback signal has exceeded 125% of rated speed.) Possible Reasons: Improperly set maximum speed parameters  Corrective Actions: Use hand tachometer to ensure proper speed and adjust the speed calibration parameter OR Possible Reasons: Wrong type of feedback selected in SPEED FBK SELECT parameter in MMI Corrective Actions: Change parameter to match feedback type OR Possible Reasons: Calibration set incorrectly on Analog Tachometer Calibration Option Board Corrective Actions: Verify calibration setting OR Possible Reasons: Improper calibration of drive speed feedback, encoder ppr selection for example  Corrective Actions: Recalibrate the speed feedback OR Possible Reasons: Improper tuning of speed loop parameters - drive overshooting or unstable Corrective Actions: Retune drive speed loop OR Possible Reasons: Coupling between motor and feedback device slipping Corrective Actions: Stop drive and isolate power, you need to check the tightness of the coupling OR Possible Reasons: Feedback device noisy or defective Corrective Actions: Replace tachometer generator (bad tach-gen) OR Possible Reasons: Bottom two LEDs on the 5701 Microtach receiver board are out Corrective Actions: Weak feedback signal intensity; check connections, fiber optic wire integrity, and transmission distances OR Possible Reasons: Field weakening parametere set incorrectly Corrective Actions: Reconfigure the field weakening parameters OR Possible Reasons: Drive operating as current regulator Corrective Actions: Check external speed loop adjustments


  • OVER VOLTS (VA) (This alarm is displayed when the motor armature voltage has exceeded 120% of rated volts) Possible Reasons: Drive miscalibrated for motor armature voltage Corrective Actions: Check armature voltage calibration matches motor name-plate information OR Possible Reasons: Drive miscalibrated for field voltage ratio (voltage model) or field current (current or field weakening model)  Corrective Actions: Check field calibration of drive. Check field current not exceeding motor nameplate data OR Possible Reasons: Armature open circuit Corrective Actions: Check armature wiring. Check armature fuse F7 (regenerative units only) OR Possible Reasons: Motor maximum speed set incorrectly causing armature voltage to exceed nameplate rating Corrective Actions: Change maximum speed parameter to match the nameplate rating OR Possible Reasons: Field weakening parameters set incorrectly if using an extended speed range motor Corrective Actions: Change field weakening parameters for use with an extended speed range motor


  • PHASE LOCK (This alarm is displayed because the drive SCR firing phase lock loop was unable to lock to supply a waveform) Possible Reasons: One or more phase of supply low, too high or missing Corrective Actions: Check all three phases of the supply, other equipment on the same supply may be unbalancing the phases. Check fuses F1,F2,F3,FS4, FS5 and FS6 OR Possible Reasons: Supply waveform badly distorted Corrective Actions: Install line chokes and/or isolation transformers if not present with drive OR Possible Reasons: Power supply pcb or control door defective Corrective Actions: Replace the power supply board OR Possible Reasons: Supply frequency outside 46-65Hz range Corrective Actions: Change supply for one within the 45 to 65Hz range


  • REMOTE TRIP Possible Reasons: Drive not set for remote operation Corrective Actions: Check setting of AUX I/O::REM. SEQUENCE parameter, also see AUX I/O-REM. SEQ. ENABLE parameter (Remote Trip flag set to zero.)


  • SPEED FEEDBACK (This means the difference between the speed feedback and armature voltage feedback is greater than the SPDFBK ALM LEVEL parameter value. If FLD WEAK ENABLE parameter is enabled, speed feedback is less than 10% when in the field weakening region) Possible Reasons: Analog tachometer feedback polarity incorrect (terminals G3 and G4)  Corrective Actions: Reverse tachometer leads, or swap encoder connections OR Possible Reasons: Armature volts miscalibrated Corrective Actions: Check armature voltage calibration setting OR Possible Reasons: Tachometer generator miscalibrated (tach-gen miscalibration) Corrective Actions: Check Analog Tachometer Calibration Option Board setting are for the proper feedback voltage at motor top speed OR Possible Reasons: Armature voltage sensing leads miswired or damaged  Corrective Actions: Check wiring of armature voltage sensing wires AS+, AS- from DC contactor to power supply board OR Possible Reasons: Coupling between motor and feedback device slipping Corrective Actions: Stop drive and isolate power, check tightness of coupling OR Possible Reasons: Feedback device noisy or defective Corrective Actions: Replace tachometer generator if noise is present while observing feedback with an oscilloscope OR Possible Reasons: Bottom two LEDs on the 5701 Microtach receiver board are out Corrective Actions: Weak feedback signal intensity; check connections, fiber optic wire integrity, ond transmission distances OR Possible Reasons: Motor has opened or shorted coils Corrective Actions: Check the motor for insulation continuity OR Possible Reasons: Analog tachometer feedback wires or shield loose or shorted to ground  Corrective Actions: Reconnect the wiring


  • STALL TRIP With motor stationary (AT ZERO SPEED parameter shows TRUE), current has exceeded the STALL THRESHOLD parameter value for longer than the STALL TRIP DELAY parameter value
    (Alarm only operates when the STALL TRIP parameter is enabled). Possible Reasons: Stall timer set too short for load acceleration Corrective Actions: Increase stall trip delay and/or install trip threshold if STALL TRIP is being used OR Possible Reasons: Field current below motor nameplate rating (if the drive is in field current control mode) Corrective Actions: Confirm motor field current with DC clamp on meter or current meter. Check drive field calibration OR Possible Reasons: Field connection miswired  Corrective Actions: Check motor field wiring is in accordance to motor prints OR Possible Reasons: Motor unable to deliver sufficient torque Corrective Actions: Check motor not undersized for load requirements OR Possible Reasons: Mechanical binding of the motor Corrective Actions: Check for mechanical problems which may cause motor to stall OR  Possible Reasons: Field voltage is not set correctly (if the drive is in field voltage control mode)  Corrective Actions: Adjust the FLD.VOLTS RATIO parameter in the Calibration section of the Parker SSD drive manual


  • THERMISTOR (This alarm means the motor temperature is too high, the motor thermistor/thermostat input is open or has high impedance. The motor must be allowed to cool in order to re-start the drive. Possible Reasons: Motor thermal protection device not wired to drive or thermistor/thermostat open circuited Corrective Actions: Check TH1 toTH2 connections to drive -connect TH1 to TH2 if motor not fitted with a thermal protection device (thermistor/thermostat) OR Possible Reasons: Blower motor rotating in wrong direction (force ventilated motors) Corrective Actions: Check direction of fan agrees with arrow on motor blower motor assembly or motor manual OR Possible Reasons: Blower filter clogged Corrective Actions: Clean or replace filter OR Possible Reasons: Motor operating at low speed/high current Corrective Actions: TEFC motors do not generate sufficient flow of air to provide sustained full load at low speed. Check gearing and/or reduce mechanical load. Use a higher power motor or provide additional cooling method independent of motor RPM OR Possible Reasons: Drive miscalibrated Corrective Actions: Check motor armature and current calibration matches motor nameplate information OR Possible Reasons: Field miswired Corrective Actions: Check motor field wiring matches motor wiring diagram for field supply


#94
Troubleshooting 101 / Re: Parker 590+ Drive Alarms
September 09, 2016, 04:56:AM
Parker 590+ Alarms and Faults

I've made a list of the 590+ alarms codes along with the possible reasons and suggestions for clearing the alarms. This is a tedious way of doing things, but hopefully it helps with your problem.


  • 3-PHASE FAILED Possible Reasons: Mains voltage incorrect Corrective Actions: Check the mains voltage of the drive (refer to Product Code). This alarm may not operate properly if the voltage is incorrect, i.e. wrong unit or drive OR Possible Reasons: Supply voltage low or missing Corrective Actions: Check auxiliary/control or main supply power OR Possible Reasons:Blown fuse Corrective Actions: Check external branch circuit protection, Check auxiliary/control fuse FT, Check that armature current calibration does not exceed drive rating  OR Possible Reasons: Loose wiring. AC contactor not engaging Corrective Actions: Check all power wiring for tightness OR Possible Reasons: Defective power supply pcb Corrective Actions: Replace power supply pcb


  • 5703 RCV ERROR Possible Reasons: Cable from drive/5703 unit not plugged into drive P3 port Corrective Actions: Check connection from drive/5703 unit to drive P3 port on control door OR Possible Reasons: 5703 unit not receiving communications from master device Corrective Actions: Check output connections and operation of master 5703 unit  OR Possible Reasons:Device not configured correctly Corrective Actions: Check configuration OR Possible Reasons: 5703 peer-to-peer communications module failure Corrective Actions: Replace 5703


  • ACCTS FAILED (Note:   The trip prevents the contactor closing and the current loop activating without armature current feedback - important in the case of external stack drives where the thyristor stack is remote from the control board.) Possible Reasons: AC current transformer plug connection to drive power board missing Corrective Actions: Check armature current transformer plug for correct installation.


  • AUTOTUNE ABORT (The Autotune sequence has been aborted. Coast Stop, Program Stop, Enable or Start/Run commands removed before AUTOTUNE procedure completed
    ) Possible Reasons: Wrong AUTOTUNE sequence followed  Corrective Actions: Repeat AUTOTUNE procedure OR Possible Reasons: AUTOTUNE incomplete. (After 2 minutes the drive will time-out if still in AUTOTUNE mode) Corrective Actions: Repeat AUTOTUNE procedure. If problem persists, contact Eurotherm (Parker SSD) Drives customer service


  • AUTOTUNE ERROR This means there was motor rotation detected during Auto-tune process (speed feedback has exceeded 20% of rated speed), or field current detected during Auto-tune (field current feedback has exceeded 6% of rated field current) (Alarm only operates during the Auto-tune sequence) Possible Reasons: Residual motor flux when field supply is disconnected Corrective Actions: Series fields are not recommended for regenerative drives and the series field winding should normally be left open circuit.  OR  Possible Reasons: Permanent magnet motor Corrective Actions: Lock motor armature and repeat Auto-tuning procedure OR  Possible Reasons: Separately supplied field Corrective Actions: Disable external field supply and repeat Auto-tuning procedure


  • CALIB INHIBIT (Calibration fault) Possible Reasons: Drive incorrectly calibrated  Corrective Actions: Check the calibration settings


  • COMMS FAULT CODE Possible Reasons: Keypad faulty Corrective Actions: Replace Keypad


  • CONFIG INHIBIT (This means the configuration procedure incomplete. CONFIGURE ENABLE is left in an enabled state) Possible Reasons: The drive was requested to start whilst in Configuration mode. Corrective Actions: Do not attempt to start the drive in Configuration mode  OR  Possible Reasons: Encoder or Micro-tach feedback option card incorrectly fitted to control door Corrective Actions: Check board fully inserted in control door OR  Possible Reasons: Fiber optic cable too long or cable distorted (bend radius too small for example) resulting in too weak a signal at Micro-tach receiver (under drive)  Corrective Actions: Reduce the tightness of the bend. The fiber optic wire should not be bent tighter than a 2" (5cm) radius  OR Possible Reasons: Fiber optic cable too short resulting in too strong a signal at Micro-tach receiver (over drive) Corrective Actions: Back the fiber optic cable out of the receive slightly and re-tighten



  • ENCODER FAILED (There is no speed feedback signal) Possible Reasons: Optional Encoder board is not fitted Corrective Actions: The SPEED FBK SELECT parameter is set to ENCODER but board not fitted OR Possible Reasons: Wire-ended encoder wires loose  Corrective Actions: Check cable and connections OR Possible Reasons: Microtach encoder wires loose or damaged Corrective Actions: Check fibre optic cable for damage,  bend radius, operating length - refer to Microtach handbook.


  • EXTERNAL TRIP (This is a customer alarm; this trip operates if input is open or high imepdance, time delay of 15 seconds)Possible Reasons: Device not wired to drive or device open circuited Corrective Actions: Check Cl to C2 connections to drive - connect Cl to C2 if customer device not fitted.


  • FIELD FAIL This alarm occurs when Field current is less than 6% of rated current when in Current Control mode or the field current is less than 50mA when in Voltage Control mode (with default current burden of 15K)  Possible Reasons: Open circuit motor field Corrective Actions: Check connection and measure field resistance OR  Possible Reasons: Faulty operation of field controller Corrective Actions: Where an ac supply feeds the onboard field regulator, check connections FL1 & FL2 for line-to-line voltage (rather than line-to-neutral) - LI into FLl, L2 into FL2.The3-phase supply must be present for mains synchronisation purposes OR  Possible Reasons: No field supply required  Corrective Actions: For loads where no field supply is required, e.g. a permanent magnet motor, set the FIELD ENABLE parameter to disable to suspend this alarm.


  • FIELD OVER I (This alarm appears because the motor field current has exceeded 120% of the calibrated value) Possible Reasons: Regulator failure Corrective Actions: Contact Parker Support OR  Possible Reasons: Badly tuned control loop (alarm only operates with field current control mode selected) Corrective Actions: Retune control loop


  • HEATSINK TRIP This simply means the drive heatsink temperature is too high, It must be allowed to cool in order to re-start the drive.

    Possible Reasons: The ambient air temperature is too high Corrective Actions: Check cooling, ambient air temperature must not exceed 40°C (104°F) for full rating OR Possible Reasons: Poor ventilation or spacing between drives Corrective Actions: Improve ventilation, if necessary reposition drives ensuring correct spacing OR  Possible Reasons: Fan failure Corrective Actions: Check fuse on power board, wrong rotation (models above 70A bridge rating)  OR  Possible Reasons: Blocked ventilation slots Corrective Actions: Clear ventilation slots OR  Possible Reasons: Clogged air filters  Corrective Actions: Clean or replace air filters  OR  Possible Reasons: Excessive armature current  Corrective Actions:  Check nominal armature current on motor nameplate against the current calibration for the drive


  • MISSING PULSE (This alarm is caused by a missing pulse from the 6-pulse armature current waveform. It trips when the motor loading exceeds 1.5 times the DISCONTINUOUS parameter value. Ripple from the speed loop from either the setpoint or feedback can cause unstable current.) Possible Reasons: Drive not Autotuned (unstable current loop)  Corrective Actions: Perform the AUTOTUNE procedure
    OR Possible Reasons: SCR gate connection loose Corrective Actions: Check SCR gate connections from the trigger board to the SCR gate leads
    OR Possible Reasons: SCR defective Corrective Actions: Check SCRs with an ohmmeter.
    OR Possible Reasons: SCR firing pcb defective Corrective Actions: Replace the pcb
    OR Possible Reasons: Motor has opened or shorted coil Corrective Actions: Check the motor with an ohmmeter and megger for insulation and continuity
    OR Possible Reasons: Coupling between motor and feedback device slipping Corrective Actions: Stop drive and isolate power - check coupling tightness
    OR Possible Reasons: Feedback device noisy or defective Corrective Actions: Replace tachometer generator if noise is present while observing feedback with an oscilloscope
    OR Possible Reasons: Bottom two LEDs on the 5701 Microtech receiver board are out Corrective Actions: Weak feedback signal intensity; check connections, fiber optic wire integrity, and transmission distances
    OR Possible Reasons: Speed loop gain too high Corrective Actions: Retune drive speed loop


  • OP STATION Possible Reasons: Keypad has been disconnected from drive whilst drive is running in local control. Corrective Actions: Do not remove under these conditions



  • OVER I TRIP (this alarm is caused by an armature overcurrent trip. The armature current has exceeded 280% of calibration value
    Possible Reasons: Drive not Autotuned (unstable current loop) Corrective Actions:The drive AUTOTUNE procedure MUST be followed for the motor the drive is to control. Repeat the AUTOTUNE procedure OR Possible Reasons: Drive incorrectly calibrated  Corrective Actions: Check the calibration settings OR Possible Reasons: Manual tuning of the drive leaves current loop unstable (THIS IS NOT RECOMMENDED!) Corrective Actions: Current loop response may be manually adjusted only AFTER AUTOTUNING is complete. Check current loop response. OR Possible Reasons: Coupling between motor and feedback device slipping  Corrective Actions: Stop drive and isolate. Check coupling tightness OR Possible Reasons: Motor armature faulty Corrective Actions: Check motor resistance to ground. Check for armature shorts OR Possible Reasons: Loss of main supply during regeneration  Corrective Actions: Check main supply branch circuit protection and SCR fuses (if existing) OR Possible Reasons: Control Door or Power Supply PCB faulty Corrective Actions: Replace defective board



(Still a few more to come...)
#95
Troubleshooting 101 / Re: SSD 590+ Alarm Question
August 19, 2016, 05:05:AM
Quote(Also, I wonder if anyone can post the complete alarm list for the 590+ SSD drives. I see they are listed on the site here for other older Parker drives.)

I can compile a list of 590+ Alarms similar to the other lists I put together, just give me some time. As for using an ohmmeter to test the field winding, I agree with testing in both places, at the motor and at the drive, just make sure you take the wires out of the terminal block at the drive first.

Another simple static test is to check for any crossover from the field winding to the armature winding. And of course, check for any continuity to ground. these tests can also be performed using a megger for more accurate results.
#96
Troubleshooting 101 / Re: Parker SSD Faults
August 12, 2016, 08:57:PM
I'm not sure of all the Parker models these faults pertain to. I am pretty sure that they are for these SSD models at least:


  • 650/00F3/230/SNN
  • 650/00F5/230/SNN
  • 650/00F7/230/SNN
  • 650/0001/230/SNN
  • 650/0002/230/SNN
  • 650/0003/230/SBN
  • 650/0005/230/SBN
  • 650/00F5/460/SBN
  • 650/00F7/460/SBN
  • 650/0001/460/SBN
  • 650/0002/460/SBN
  • 650/0003/460/SBN
  • 650/0005/460/SBN
  • 650/0007/460/SBN
  • 650/0010/460/SBN
#97
Here's the Westinghouse HL71B troubleshooting guide, most of which can be found in the Linatrol service manual. I just listed out the possible scenarios along with the general reason for a fault. If you have more specific questions about solving problems with the HL71B, just ask and I'll see what I can suggest.


  • Tracing lamp does not light and tracer will not acquire pattern; tra­verse normal. : Possible Faults: Defective photo-transistor, Defective FET, Shorted or open wiring, Flood lamps not lit. Inadequate Signal, or No 'On-Pattern' signal or 'Sample' pulses

  • Tracer will not trace, tracing lamp is lit and traverse is normal.Possible Faults: MODE relay K1 output, Sample and Hold signal outputs, or 'On Pattern' relay is not latching

  • Tracer reversal on pattern; traverse normal : Possible Faults: 'On Pattern' relay K2 is not latching, Poor Pattern, Focus incorrect, Low Signal, Insufficient illumination, Defective photo-transistor Q1 or FET Q2, Signal voltage level, or Sine/Cosine generator outputs

  • Tracer will not trace in the Y axis : Possible Faults: 'Inhibit' or 'Sample', Drive lost in Y axis, No Cosine Signal, MODE relay K1 output, or No 'Y-speed' signal

  • Tracer will not trace in the X axis : Possible Faults:  Drive lost in X axis, No Sine Signal, MODE relay K1 output, or No 'X-speed' signal

  • Machine will not drive the Y axis : Possible Faults: No signal input to 'Y' Servo Amplifier Card, No Signal input to 'Y' Power Amplifier card, No drive signal to motor, Faulty motor, Slippage in Y-axis drive mechanism, or Machine 'Y' limit switches activated

  • Machine will not drive the X axis : Possible Faults:  No signal input to 'X' Servo Amplifier card, No signal input to 'X' Power Output Assembly, No drive signal to motor, Faulty motor, Slippage in X-axis drive mechanism, or the Machine 'X' limit switches are activated

  • Tracer con­tinually burns out Power Trans­istors on Power Ampli­fier Assembly : Possible Faults:  Amplifier current limiting not functioning

  • Flood lights and indicator lights do not light : Possible Faults: the19V supply is not functioning

  • Power light (DS1) does not light : Possible Faults: Mains input 9 (could be blown fuses or power problems upstream)

  • Preamplifier, Logic and Sample and Hold cards disabled : Possible Faults: +/-24V DC Supplies, +/-30V DC Supplies

  • Servo Ampli­fiers and Power Amplifier Assemblies disabled : Possible Faults: +/-24V 1C Regulators,+/-30V DC Supplies


Good Luck and happy troubleshooting!
#98
I can list out some of the HL71B troubleshooting guide that I have in our Linatrol service manual. Maybe this will send you in the right direction without having a HL71B service manual of your own.

The HL71B can have many applications, ours in in an automated torching machine. Lets' start with the alignment guide which is always helpful. It may point you in the right direction or it might be useful in the future if you continue to use the HL71B as your control. This part may or may not pertain to your machine.


  • Cannot set Preamplifier offsets to zero : Things to check: Is MODE relay (K1) removed, possible Preampliifer card may be defective

  • Cannot set Sample & Hold offsets to zero : Things to check: Is MODE relay (K1) removed, Are Preamplifier offsets zero, Is Tracing light on, possibly Sample and Hold card may be defective

  • Cannot set Servo Amplifier offsets to zero : Things to check: Is MODE relay (K1) removed, Are Sample and Hold offsets zero, Is Tracing light on, Is "On Pattern" relay (K2) defective, Is Power Amplifier unit defective, also Servo Amplifier card may be defective

  • Traverse Speed  Signals  incorrect : Things to check: Is Direction switch in correct position, Is MODE switch in center position, Is Gas Mode switch in correct position, Is SPEED control defective, possible Sample and Hold card may be defective

  • Tracing Speed  Signals  incorrect, cannot adjust Sample & Hold output : Things to check: Is Tracing light illuminated, Is MODE relay (K1) plugged in, Is scanner motor turning, Are generators defective, Is Preamplifier card defective, Is the Sample and Hold card defective

  • Cannot adjust machine  speed : Things to check: Are Servo Amplifier offsets zero, Is Power Amplifier unit defective, Is Servo Amplifier defective, Is motor defective, Is tachometer defective, Is gearbox defective, Is gear coupling defective

There's more to come as soon as I can put it together and get it posted.
#99
My rule is one failure is possible with any brand of motor, drive, or encoder system, it happens... But when you repeatedly have problems with damaged components in your drive system, then you should take a second look at the installation and other factors that surround the system.
#100
Troubleshooting 101 / Re: Parker SSD Faults
August 05, 2016, 04:36:AM
I compiled a list of the faults that are listed in the SSD drive manual along with a few simple suggestions for clearing them. This is the for the 650 series but it may actually be valid for other models, you'll have to determine that on your own.


  • dCH1 OVERVOLTAGE: The drive internal dc link voltage is too high; possible reasons for fault: the supply voltage is too high, You're trying to decelerate a large inertia load too quickly, DECEL TIME time too short, or The brake resistor is open circuit

  • dCLO UNDERVOLTAGE: DC link low trip; which means the supply vltage is too low, test and troubleshoot with a voltmeter.

  • i HI OVERCURRENT: The motor current being drawn from the drive is too high; There are many possible reasons for this fault:You're trying to accelerate a large inertia load too quickly, ACCEL TIME time too short, you're trying to decelerate a large inertia load too quickly, DECEL TIME time too short, Application of shock load to motor, Short circuit between motor phases, Short circuit between motor phase and earth (ground), Motor output cables too long or too many parallel, motors connected to the drive, or FIXED BOOST level set too high.

  • HOt HEATSINK: The ambient air temperature is too high, poor ventilation or spacing between drives. This fault is caused by improper installation or inadequate cooling.

  • Et EXTERNAL TRIP: The external trip input is high, Check configuration to identify the source of the signal (non-standard configuration).

  • It INVERSE TIME: A prolonged overload condition, exceeding the Inverse Time allowance, has caused the trip which means you must find and remove the overload condition.

  • LOOP CUURENT LOOP: A current of less than 1mA is present when 4-20mA setpoint is selected, in this case, look for a broken wire or a loose connection.

  • StLL MOTOR STALLED: The motor has stalled (not rotating) Drive in current limit >200 seconds; possible causes for this fault: The motor loading is too great or FIXED BOOST level set too high.

  • t 3 ANIN FAULT: AIN2 overload on terminal 3: Overcurrent applied in Current mode to terminal 3, remove or correct source of overcurrent.

  • dISP DISP/KEYPAD: Keypad has been disconnected from drive while drive is running in Local Control; simply means the keypad was accidentally disconnected from drive  (indicated over Comms, or by a second keypad).

  • SCI LOST COMMS: Lost communications; possible causes for communication fault: COMMS TIMEOUT parameter set too short, Master device failed, The wiring is broken, or there is an incorrect comms setup.

  • CntC CONTACTOR FEEDBACK: Contactor feedback signal lost: Check connection to the terminal wired to "contactor closed" parameter in Sequencing Logic (non-standard configuration).

  • Ot MOTOR OVERTEMP: The motor temperature is too high; possible causes for this fault: Excessive load, the motor voltage rating incorrect, FIXED BOOST level set too high, Prolonged operation of the motor at low speed without forced cooling, Break in motor thermistor connection.
  • I HI CURRENT LIMIT: Software overcurrent trip; If the current exceeds 180% of stack rated current for a period of 1 second, the drive will trip. This fault is caused by shock loads. Remove the shock load and test. Possible causes for this fault include ACCEL TIME and/or FIXED BOOSTset too high, or DECEL TIME set too low, so it can be cleared by making adjustments to the drive calibration.

  • LSPd LOW SPEED OVER I: The motor is drawing too much current (> 100%) at zero output frequency; This fault is caused by FIXED BOOST level set too high.


  • t 4 10V FAULT: +10V REF overload warning (terminal 4), it is a 10mA maximum, use a multimeter to determine the source of the overcurrent.


  • Shrt DESATURATION: Desaturatlon has occurred; this is iInstantaneous overcurrent. Refer to OVERCURRENT fault for more info on clearing this fault.


  • dCRP DC LINK RIPPLE: The DC link ripple voltage is too high; possible cause for this fault would be a missing phase, check incoming power supply for all three phases.


  • dbSC BRAKE SHORT CCT: Brake resistor overcurrent; Check the brake resisitor value is greater than the minimum allowed.


  • t 5 ANOUT FAULT: AOUT overload at terminal 5; check for current at terminal 5, it is rated for 10mA max.


  • t 9 DIGIO 1 (T9) FAULT: DIN3 overload on Terminal 9; check for too much current, it is rated 20mA max, use a multimeter to determine the cause of the overcurrent.


  • t 10 DIGIO 2 (T10) FAULT: DOUT2 overload at terminal 10; check for overload since max current for this output is rated at 50mA.


  • trIP UNKNOWN: Unknown trip with unknown cause (I got this from the manual)

  • ICAL ICAL: Zero I current calibration; current sensor calibration fault, cycle the power to the drive, if persistent contact factory or replace the drive.


  • COdE PRODUCT CODE ERROR: Switch the drive off and back on (cycle power), if it is persistent, replace drive/ contact factory or your Parker SSD rep.


  • CAL CALIBRATION DATA ERROR: Switch the drive off and back on (cycle power), if it is persistent, replace drive/ contact factory or your Parker SSD rep.


  • dATA CONFIGURATION DATA FAILURE: Press the "E" button to accept the default configuration, if this fault persists, contact the factory or replace the drive.
#101
Here's the F7000's, F8000's, and F9000's:

The F7000's:


  • F7010 Safety related limited increment exceeded
  • F7011 Safety rel. position limit val., exc. in pos. dir
  • F7012 Safety rel. position limit val., exc. in neg. dir
  • F7013 Velocity threshold exceeded
  • F7014 Acceleration threshold exceeded
  • F7020 Safety related maximum speed exceeded
  • F7021 Safety related end position exceeded
  • F7030 Pos. window for safety rel. operational stop exceeded
  • F7031 Incorrect direction of motion
  • F7040 Validation error parameterized - effective threshold
  • F7041 Actual position value validation error
  • F7042 Validation error of safety related operating mode
  • F7043 Error of output stage interlock
  • F7050 Time for stopping process exceeded
  • F7051 Safety related deceleration exceeded

The F8000's:


  • F8000 Fatal hardware error
  • F8010 Autom. commutation: max. motion range when moving back
  • F8011 Commutation offset could not be determined
  • F8012 Autom. commutation: max. motion range
  • F8013 Automatic commutation: current too low
  • F8014 Automatic commutation: overcurrent
  • F8015 Automatic commutation: timeout
  • F8016 Automatic commutation: iteration without result
  • F8017 Automatic commutation: incorrect commutation adjust
  • F8022 Enc. 1: enc. signals incorr. (can be cleared in ph. 2)
  • F8023 Error mechanical link of encoder or motor connection
  • F8025 Overvoltage in power section
  • F8027 Safety related standstill while drive enabled
  • F8028 Overcurrent in power section
  • F8042 Encoder 2 error: signal amplitude incorrect
  • F8057 Device overload shutdown
  • F8060 Overcurrent in power section
  • F8064 Interruption of motor phase
  • F8067 Synchronization PWM-Timer wrong
  • F8069 +/-15Volt DC error
  • F8070 +24Volt DC error
  • F8076 Error in error angle loop
  • F8078 Speed loop error
  • F8079 Velocity limit value exceeded
  • F8091 Power section defective
  • F8100 Error when initializing the parameter handling
  • F8102 Error when initializing power section
  • F8118 Invalid power section/firmware combination
  • F8120 Invalid control section/firmware combination
  • F8122 Control section defective
  • F8129 Incorrect optional module firmware
  • F8130 Firmware of option 2 of safety technology defective
  • F8133 Error when checking interrupting circuits
  • F8134 Safety related holding system: fatal error
  • F8135 Velocity exceeded with trend monitoring
  • F8140 Fatal CCD error
  • F8201 Safety command for basic initialization incorrect
  • F8203 Safety technology configuration parameter invalid
  • F8813 Connection error mains choke
  • F8838 Overcurrent external braking resistor

The F9000's:


  • F9001 Error internal function call
  • F9002 Error internal RTOS function call
  • F9003 Watchdog
  • F9004 Hardware trap

Good Luck!!
#102
Rexroth Indradrive Fatal Errors (Fault Codes)

Here is a simple list of fatal errors that I have from one of the older Rexroth Indramat drives. These are the fatal errors, the way I always understood it, F means "failure" or "fatal" when it comes to the Rexroth Fault Codes. I broke the list into sections per thousands (ie F2000's, F3000's, F4000's, etc) and I broke this list into two posts since it might be too big to put into one.

The F2000's:


  • F2003 Motion step skipped
  • F2004 Error in motion profile
  • F2005 Cam shaft invalid
  • F2006 MMC was removed
  • F2007 Switching to non-initialized operating mode
  • F2008 RL The motor type has changed
  • F2009 PL Load parameter default values
  • F2010 Error when initializing digital I/O
  • F2011 PLC-Error nr. 1
  • F2012 PLC-Error nr. 2
  • F2013 PLC - Error nr. 3
  • F2014 PLC - Error nr. 4
  • F2018 Device overtemperature shutdown
  • F2019 Motor overtemperature shutdown
  • F2021 Motor temperature monitor defective
  • F2022 Device temperature monitor defective
  • F2025 Drive not ready for Control
  • F2026 Undervoltage in power section
  • F2027 Excessive oscillation in DC bus
  • F2028 Excessive deviation
  • F2031 Encoder 1 error: signal amplitude incorrect
  • F2032 Validation error during commutation fine adjust   
  • F2033 External power supply X10 error
  • F2036 Excessive position feedback difference
  • F2037 Excessive position command difference
  • F2039 Maximum acceleration exceeded
  • F2040 Device overtemperature 2 shutdown
  • F2042 Encoder 2: encoder signals incorrect   
  • F2043 Measuring encoder: encoder signals incorrect
  • F2044 External power supply X15 error
  • F2048 Low battery voltage
  • F2050 Overflow of target position preset memory
  • F2051 No sequential block in target position preset memory
  • F2053 Incr. encoder emulator: pulse frequency too high
  • F2054 Incr. encoder emulator: hardware fault
  • F2055 External power supply X31/X32 error
  • F2057 Target position out of travel range
  • F2058 Internal overflow by positioning input
  • F2059 Incorrect command value direction when positioning
  • F2063 Internal overflow master axis generator
  • F2064 Incorrect cmd value direction master axis generator
  • F2067 Synchronization to master communication incorrect
  • F2069 Error when releasing the motor holding brake
  • F2074 Actual pos. value 1 outside absolute encoder window
  • F2075 Actual pos. value 2 outside absolute encoder window
  • F2076 Actual pos. value 3 outside absolute encoder window
  • F2077 Current measurement trim wrong
  • F2086 Error supply module
  • F2087 Module group communication error
  • F2100 Incorrect access to command value memory
  • F2101 It was impossible to address MMC
  • F2102 It was impossible to address I2C memory
  • F2103 It was impossible to address EnDat memory
  • F2104 Commutation offset invalid
  • F2105 It was impossible to address Hiperface memory
  • F2110 Error in non-cyclical data communic. of power section
  • F2120 MMC: defective or missing, replace
  • F2121 MMC: incorrect data or file, create correctly
  • F2122 MMC: incorrect IBF file, correct it
  • F2123 Retain data backup impossible
  • F2124 MMC: saving too slowly, replace
  • F2130 Error comfort control panel
  • F2140 CCD slave error
  • F2150 MLD motion function block error
  • F2174 Loss of motor encoder reference
  • F2175 Loss of optional encoder reference
  • F2176 Loss of measuring encoder reference
  • F2177 Modulo limitation error of motor encoder
  • F2178 Modulo limitation error of optional encoder
  • F2179 Modulo limitation error of measuring encoder
  • F2190 Incorrect Ethernet configuration
  • F2260 Command current limit shutoff
  • F2270 Analog input 1 or 2, wire break
  • F2802 PLL is not synchronized
  • F2814 Undervoltage in mains
  • F2815 Overvoltage in mains
  • F2816 Softstart fault power supply unit
  • F2817 Overvoltage in power section
  • F2818 Phase failure
  • F2819 Mains failure
  • F2820 Braking resistor overload
  • F2821 Error in control of braking resistor
  • F2825 Switch-on threshold braking resistor too low
  • F2833 Ground fault in motor line
  • F2834 Contactor control error
  • F2835 Mains contactor wiring error   
  • F2836 DC bus balancing monitor error
  • F2837 Contactor monitoring error
  • F2840 Error supply shutdown
  • F2860 Overcurrent in mains-side power section
  • F2890 Invalid device code
  • F2891 Incorrect interrupt timing
  • F2892 Hardware variant not supported

The F3000's:


  • F3111 Refer, missing when selecting safety related end pos
  • F3112 Safety related reference missing
  • F3115 Error, brake check time interval exceeded
  • F3117 Actual position values validation error
  • F3122 Safety related holding system: system error
  • F3123 Safety related holding system: brake check missing
  • F3130 Error when checking input signals
  • F3131 Error when checking acknowledgment signal
  • F3132 Error when checking diagnostic output signal
  • F3133 Error when checking interrupting circuits
  • F3134 Dynamization time interval incorrect
  • F3135 Dynamization pulse width incorrect
  • F3140 Safety parameters validation error
  • F3141 Selection validation error
  • F3142 Activation time of enabling control exceeded
  • F3143 Safety command for clearing errors incorrect
  • F3144 Incorrect safety configuration
  • F3145 Error when unlocking the safety door
  • F3146 System error channel 2
  • F3147 System error channel 1
  • F3150 Safety command for system start incorrect
  • F3151 Safety command for system halt incorrect
  • F3152 Incorrect backup of safety technology data
  • F3160 Safety bus communication error

The F4000's:


  • F4001 Sync telegram failure
  • F4002 RTD telegram failure
  • F4003 Invalid communication phase shutdown
  • F4004 Error during phase progression
  • F4005 Error during phase regression
  • F4006 Phase switching without ready signal
  • F4009 Bus failure
  • F4012 Incorrect I/O length
  • F4016 PLC double real-time channel failure
  • F4017 S-lll: incorrect sequence during phase switch
  • F4034 Emergency-Stop
  • F4140 CCD communication error

The F6000's:


  • F6010 PLC Runtime Error
  • F6024 Maximum braking time exceeded
  • F6028 Position limit value exceeded (overflow)
  • F6029 Positive travel limit exceeded
  • F6030 Negative travel limit exceeded   
  • F6034 Emergency-Stop
  • F6042 Both travel range limit switches activated
  • F6043 Positive travel range limit switch activated
  • F6044 Negative travel range limit switch activated
  • F6140 CCD slave error (emergency halt)

#103
In general, Bus Inhibit Alarm means the the DC bus has been disabled due to an overvoltage. DC bus overvoltages sometime come from too much inertia which overwhelms the regen circuit. It can also be inhibited thanks to an internal drive fault such as component failure.
#104
You can take this alarm literally. Motor Slow Response simply means that the motor is not responding to the command signal fast enough. This can generally be solved with motor tuning...

Get out your scope... If you look at you waveform as the motor makes its move, you'll see it approach its destination very cautiously. The motor will have to be tuned to be more aggressive. Consult your manuals for tuning procedure and get to it!
#105
Troubleshooting 101 / Re: AC Tech Drive Faults
July 24, 2016, 05:54:AM
AC Tech VFD Fault List | Lenze Drive Faults | AC Tech Drive Alarms

Here are some of the more common AC Tech faults, these faults, or alarms, pertain to many models:


  • F_AF : High Temperature Fault
  • F_AL : Assertion Level Fault
  • F_bF : Personality Fault
  • F_CF : Control Fault
  • F_cF : Incompatible EPM Fault
  • F_cFt : Forced Translation Fault
  • F_dbF : Dynamic Braking Fault
  • F_EF : External Fault
  • F_F1 : EPM Fault
  • F_F2 : Internal Fault
  • F_F3: Internal Fault
  • F_F4: Internal Fault
  • F_F5 : Internal Fault
  • F_F6 : Internal Fault
  • F_F7 : Internal Fault
  • F_F8 : Internal Fault
  • F_F9 : Internal Fault
  • F_F10 : Internal Fault
  • F_F11 : Internal Fault
  • F_F12 : Internal Fault
  • F_Fnr : Control Configuration Fault
  • F_FoL : TB25 Threshhold Fault
  • F_GF : OPM Defaults Data Fault
  • F_HF : High DC Bus Voltage Fault
  • F_IL : Digital Input Configuration Fault
  • F_JF : Remote Keypad Fault
  • F_LF : Low DC Bus Voltage Fault
  • F_nId : No Motor ID Fault
  • F_ntF : Module Communication Fault
  • F_nF1 : Network Fault
  • F_nF2 : Network Fault
  • F_nF3 : Network Fault
  • F_nF4 : Network Fault
  • F_nF5 : Network Fault
  • F_nF6 : Network Fault
  • F_nF7 : Network Fault
  • F_nF8 : Network Fault
  • F_nF9 : Network Fault
  • F_OF : Output Fault (Transistor Fault)
  • F_OF1 : Output Fault (Ground Fault)
  • F_PF : Motor Overload Fault
  • F_rF : Flying Restart Fault
  • F_SF : Single Phase Fault
  • F_UF : Start Fault
  • F_FRU : TB5 Threshhold Fault