Don't want to sound pushy but I'm looking for a quick response... I'm getting a fault: F552 on an ABB DCS800 drive. Came on suddenly and I have to resolve this quick. if anyone has info on ABB DCS drive faults, please post!
Thanks,
Dave
Here's a general list of ABB faults and alarms for the DCS drive manual, they should pertain to all these models:
DCS800-EP1-0020-05, DCS800-EP2-0025-05, DCS800-EP1-0045-05, DCS800-EP2-0050-05, DCS800-EP1-0065-05, DCS800-EP2-0075-05, DCS800-EP1-0090-05, DCS800-EP2-0100-05, DCS800-EP1-0125-05, DCS800-EP2-0140-05, DCS800-EP1-0180-05, DCS800-EP2-0200-05, DCS800-EP1-0230-05, DCS800-EP2-0260-05, DCS800-EP1-0315-05, DCS800-EP2-0350-05,  DCS800-EP1-0405-05, DCS800-EP2-0450-05, DCS800-EP1-0470-05, DCS800-EP2-0520-05, DCS800-EP1-0610-05, DCS800-EP2-0680-05, DCS800-EP1-0740-05, DCS800-EP2-0820-05,
DCS800-EP1-0900-05, DCS800-EP2-1000-05, DCS800-EP2-1010-05
Here's the ABB DCS Fault List:
  • F501 - Auxiliary Undervoltage Limit
    The auxiliary voltage is too low at terminal X99 on PIN-4 or POW-4 Board.
  • F502 - Armature Overcurrent
    The armature current exceeds the overcurrent limit.
  • F503 - Armature Overvoltage
    The armature voltage exceeds the overvoltage limit
  • F504 - Converter Overtemperature
    The drive internal temperature exceeds the temperature limit.
  • F505 - Residual current detection
    The drive has detected a ground fault.
  • F506 - Motor 1 Overtemperature
    The motor 1 temperature exceeds the temperature limit.
  • F507 - Motor 1 Overload
    Motor overloaded based on calculated thermal curve.
  • F508 - Input/Output Board Not Found or Faulty
    The drive cannot communicate with a previously known option board such as COM-8x, RAIO, RDIO, IOB-2, IOB-3, RTAC, or DSL-4.
  • F509 - Motor 2 Overtemperature
    The motor 2 temperature exceeds the temperature limit.
  • F510 - Motor 2 Overload
    The motor 2 current exceeds the overload limit.
  • F512 - Mains Low Voltage
    The mains voltage is below the fault limit or the mains voltage is below the alarm limit for an excessive amount of time
  • F513 - Mains Overvoltage
    The mains voltage is above the fault limit for more than 10 seconds.
  • F514 - Mains Not in Sync
    The synchronization with the mains frequency has been lost.
  • F515 - Motor 1 Field Supply (Exciter) Overcurrent
    The field current is above the fault limit.
  • F516 - Motor 1 Field Supply (Exciter) Communication Loss
    DSL-Link communication between the drive and the field supply (Exciter) has stopped for a time longer than the fault limit.
  • F517 - Armature Current Ripple
    Current ripple on the DC output exceeds the limit. This is often an indication that one or more thyristors is not working or a fuse is blown.
  • F518 - Motor 2 Field Supply (Exciter) Overcurrent M
  • F519 - Motor 2 Field Supply (Exciter) Communication Loss
  • F521 - Field Exciter Missing (Selected Motor)
    One or more field supply (exciter) faults is present for the motor currently selected (M1 or M2), including: (for M1) F515, F516, F529, F537 and/or F541; (for M2) F518, F519, F530, F538 and/or F542.
  • F522 - Speed Feedback (Selected Motor)
    Speed feedback from a tachometer or encoder is continuously compared to EMF feedback while running. A fault indicates that the EMF was above a limit (30.15) while the motor speed was below a limit (30.14).
  • F523 - External Fan Acknowledge Missing
    The Fan Acknowledge digital input was lost or was not set within 10 seconds.
  • F524 - Main Contactor Acknowledge Missing
    The Main Contactor Acknowledge digital input was lost or was not set within 10 seconds.
  • F525 - Type Code Mismatch
    On D1, D2, D3, or D4 modules, the current and voltage range of the type code setting is limited to 1000 Adc and 600 Vac. A fault indicates the existing setting is out of range.
  • F526 - External Fault Via Digital Input
    The External Fault digital input was set
  • F527 - Converter Fan Acknowledge Missing
    The Converter Fan Acknowledge digital input was lost or was not set within 10 seconds.
  • F528 - Fieldbus Communications Loss
    Fieldbus Communications have been interrupted for a period longer than a time limit after the first data set from the overriding control has been received.
  • F529 - Motor 1 Field Supply (Exciter) not OK
    A fault was detected by the motor 1 field supply (exciter) during its self diagnosis or there was a power failure in field supply 1.
  • F530 - Motor 2 Field Supply (Exciter) not OK
    A fault was detected by the motor 2 field supply (exciter) during its self diagnosis or there was a power failure in field supply 2.
  • F531 - Motor Stalled (Selected Motor)
    The measured speed is less than the stall speed and the torque is greater than the stall torque for a time greater than the stall time.
  • F532 - Motor Overspeed (Selected Motor)
    The measured speed of the selected motor exceeded the respective overspeed limit.
  • F533 - 12 Pulse Reversal Timeout
    On 12-pulse systems, armature current direction did not change for a period longer than a time limit after zero current has been detected.
  • F534 - 12 Pulse Current Difference
    For systems configured for 12-pulse parallel operation, the current difference has exceed the limit for a period longer than the limit.
  • F535 - 12 Pulse Communication
    On 12-pulse systems, DCS-Link communications between the master and the follower drive have been interrupted for a period longer than the limit.
  • F536 - 12 Pulse Follower Failure
    A fault has been generated in the 12-pulse follower
  • F537 - Motor 1 Field Supply (Exciter) ready lost
    Motor 1 field supply (exciter) has lost the ready-foroperation message while running. The AC supply voltage may be missing or no longer in sync.
  • F538 - Motor 2 Field Supply (Exciter) ready lost
    Motor 2 field supply (exciter) has lost the ready-for operation message while running. The AC voltage may be missing or no longer in sync.
  • F539 - Fast Current Rise
    The current through the drive has risen too quickly, exceeding the limit. This may be caused by a short circuit or incorrect tuning.
  • F540 - SDCS-COM-8 Faulty
    The SDCS-COM-8 board is no longer operable
  • F541 - Motor 1 Field Exciter Low Current
    The motor 1 field current is below the current limit for a period longer than a time limit.
  • F542 - Motor 2 Field Exciter Low Current
    The motor 2 field current is below the current limit for a period longer than a time limit.
  • F543 - SDCS-COM-8 Communication Loss
    Overriding control and/or master-follower communications through channel 0 or 2 of the COM-8 have been interrupted for a period longer than the limit.
  • F544 - Peer to Peer, Master-Follower Communication Loss
    DCS-Link for fieldbus communications have been interrupted for a period longer than the limit.
  • F545 - Application Load Failure
    The application program did not load correctly.
  • F546 - Local Command Loss
    Communications have been interrupted with the control panel, Drive Window, or Drive Window light while in Local Control Mode.
  • F547 - Hardware Failure
    Hardware failure has been detected.
  • F548 - Firmware Failure
    Firmware failure has been detected or firmware did not load correctly.
  • F550 - Parameter or Memory Card Read Error
    Reading the actual parameter set or a user parameter set from either flash or the Memory Card failed. Check that User1 and/or User2 have been saved properly using ApplMacro (99.08). Also check the SDCS-MEM-8 memory card. May also require replacing the SDCSCON-4 board.
  • F551 - Analog Input Out of Range
    One of the analog input values is below the minimum limit.
  • F552 - Mechanical Brake (Selected Motor)
    The acknowledge signal for brake open or brake engaged is missing for a period longer than the open or engage limit.
  • F553 - Tachometer or Encoder Polarity (Selected Motor)
    Speed feedback polarity from a tachometer or encoder is continuously compared to EMF feedback polarity while running. A fault indicates that the two ran in opposite directions while the motor feedback speed and EMF speed were above absolute limits. If this occurred during start up, try reversing polarity of the motor or the tach/encoder. If this occurred while in production, the tach/encoder may be faulty.
  • F554 - Tachometer Range (Selected Motor)
    The signal from the tachometer analog input has exceeded a limit. If this occurred during start up, connect the tach to the next higher voltage terminal on drive connector X3 terminals 1, 2 or 3.
  • F556 - Torque Proving (Selected Motor)
    The TorqProvOK signal has not been set within a time limit after the RUN command (7.01 bit3) has been set.
  • F557 - Reversal Time
    Armature current direction did not change for a period longer than a time limit after zero current was detected. For motors with high inductance (e.g., large motors) or if motor is high voltage compared to the mains voltage, try decreasing RevDly (43.14), then increasing the limit
Stay tuned for the DCS alarms...
And here's the ABB DCS Alarm List:
  • A101 - Coast Stop (Off2) via Digital Input
    The Coast Stop (Off2) digital input is cleared.
  • A102 - Emergency Stop (Off3) via Digital Input
    The Emergency Stop (Off3) digital input is cleared.
  • A103 - DC Breaker Acknowledge Missing (Selected Motor)
    The DC Breaker Acknowledge digital input is cleared.
  • A104 - Converter Overtemperature
    The drive internal temperature is within 5°C of the temperature limit.
  • A105 - Dynamic Braking in progress
    For non-US dynamic braking, the DynBrakeAck input is set while in the ON state
  • A106 - Motor 1 Overtemperature
  • A107 - Motor 1 Overload
    The motor 1 current exceeds the overload limit.
  • A109 - Motor 2 Overtemperature
  • A110 - Motor 2 Overload
  • A111 - Mains Low Voltage
    The mains voltage is below the alarm limit.
  • A112 - Peer to Peer, Master-Follower Communication Loss
    DCS-Link or fieldbus communications have been interrupted for a period longer than the limit.
  • A113 - SDCS-COM-8 Communication Loss
  • A114 - Armature Current Deviation
    Current reference differs from current actual by more than a limit for longer than a time limit. See alarm description in DCS800 Firmware Manual for what to check in the event of a fault.
  • A115 - Tachometer Range (Selected Motor)
    If this alarm is present for longer than 10 seconds, the signal from the tachometer analog input exceeded a limit. If present for 10 seconds and then it clears, it is an indication that M1OvrSpeed (30.16) or M2OvrSpeed (49.21) has changed and a new tach fine tuning is required.
  • A116 - Mechanical Brake (Selected Motor)
    Active only when BrakeFaultFunc (42.06) = CRANE, the acknowledge signal for brake engaged is missing for a period longer than the engage limit.
  • A117 - Armature Current Ripple
    DC current ripple exceeds the limit. If this occurs during start up, then current controller gain may be set too high. Otherwise, this is often an indication that one or more thyristors is not working or a fuse is blown.
  • A118 - Found New Application on Memory Card
    An application has been found on SDCS-MEM8 used with ControlBuilder.
  • A119 - Application Mismatch between Drive and Memory Card
    The applications previously loaded to the drive and the one on the SDCS-MEM8 do not match.
  • A120 - Overvoltage Protection Active
    The overvoltage protection unit, DCF506-xxxx-51 is active, so the controller is blocking the converter output.
  • A121 - Autotuning Failed
    Autotuning has failed.
  • A122 - Mechanical Brake (Selected Motor)
    Active only when BrakeFaultFunc (42.06) ? FAULT, the acknowledge signal for brake open or brake engaged is missing for a period longer than the open or engage limit. Or torque actual does not reach the torque limit, used, for example, for cranes with a hanging load.
  • A124 - Speed Scaling Out of Range
    See: Motor 1: 50.01, 20.01, 20.02, 99.04 and Motor 2: 49.22, 49.03, 49.19, 49.20
  • A125 - Speed Feedback (Selected Motor)
    Speed feedback from a tachometer or encoder is continuously compared to EMF feedback while running. A fault indicates that the EMF voltage was above a voltage limit (30.15) while the motor speed was below a speed limit (30.14). This usually indicates there is a problem with the tachometer or encoder.
  • A126 - External Alarm via Digital Input
    The External Alarm digital input is set.
  • A127 - Analog Input Out of Range
  • A128 - Fieldbus Communications Loss
  • A129 - Parameters Restored
    The parameters found in flash were invalid at power-up (checksum fault). All parameters were restored from the parameter backup.
  • A130 - Local Command Loss
    Communications have been interrupted with the control panel, Drive Window, or Drive Window Light while in Local Control Mode
  • A131 - Parameter Added
    A new firmware program with a different amount of parameters was downloaded. The new parameters are set to their default value.
  • A132 - Parameter Setting Conflict
    The settings of some parameters are in conflict with each other.
  • A133 - Retained Data Invalid
    The retained data was invalid at power-up; the backup data was used. Backup data reflects the status during the previous power-up. Retained data includes: fault logger data, Data1 (19.01) thru Data4 (19.04), I/O options (see group 98), parameters defined by means of DCS800 ControlBuilder when the RETAIN box is checked.
  • A134 - Parameter Compatibility
    When downloading parameter sets or during powerup the firmware attempts to write the parameters. If setting of a parameter is not possible or not compatible, the parameter is set to default.
  • A135 - Parameter Upload or download Failed
    The checksum verification failed following a parameter upload or download. Please try again
  • A136 - Adaptive Program Task Time Not Set
    The task time for Adaptive Programming is not set when the user attempted to start it.
  • A137 - Speed Not Zero
    Drive was restarted before the motor decelerated below the zero speed limit.
  • A138 - Off2 (Coast Stop) Fieldbus
    Bit 1 from the main control word is not set, causing a start inhibit condition.
  • A139 - Off3 (Emergency Stop) Fieldbus
    Bit 2 from the main control word is not set, causing an estop condition.
  • A140 - Illegal Fieldbus Settings
    The fieldbus parameters in group 51 (fieldbus) are not set according to the fieldbus adapter or the device has not been selected.
  • A141 - SDCS-COM8 Firmware Version Conflict
    Invalid combination of drive (SDCS-CON-4) firmware and SDCS-COM-8 firmware. Drive firmware 3.7 is compatible with SDCS-COM-8 firmware 1.80 or higher. See firmware release notes for complete compatibility list. Typically requires upgrading to a newer SDCSCOM-8 board
  • A142 - Memory Card Missing
    A ControlBuilder application has been loaded in the drive but the memory card belonging to that application has not been found.
  • A143 - Memory Card Failure
    The data found in the memory card was invalid (checksum fault).
dave2
Many thanks, it was just a simple braking issue.